I know that NEC requested a complete empty conduit system to start pulling wires. Could you address me to the article / paragraph number. Thanks a lot.
300.18 Raceway Installations.
(A) Complete Runs. Raceways, other than busways or ex-
posed raceways having hinged or removable covers, shall be
installed complete between outlet, junction, or splicing points
prior to the installation of conductors. Where required to fa-
cilitate the installation of utilization equipment, the raceway
shall be permitted to be initially installed without a terminat-
ing connection at the equipment. Prewired raceway assemblies
shall be permitted only where specifically permitted in this
Code for the applicable wiring method.
Exception: Short sections of raceways used to contain
conductors or cable assemblies for protection from physi-
cal damage shall not be required to be installed complete
between outlet, junction, or splicing points.
The raceway needs to be complete to prevent damage to the conductors. This one gets violated daily. :roll: