Hi,
Can I use 6"x6"x24" Huffman gutter for intercepting a feeder composed of 2" EMT that includes 4 #3/0 plus grounding cond...


Wires were short during measuring/cutting/ pulling...

Thank you
 

Smart $

Esteemed Member
Location
Ohio
If it's straight through then you need a minimum of 2" * 8 or, 16" in length.
If by intercept he means to splice the conductors, it only needs to be 6 times the conduit size... but sizing for straight pull at 8 times would be prudent if the run is ever re-pulled.
 