GFCI NEEDED

Status
Not open for further replies.
422.52 Electric Drinking Fountains. Electric drinking fountains
shall be protected with ground-fault circuit-interrupter
protection.

Wait you said under. Does the receptacle feed/serve the fountain?
 
Last edited:
422.52 Electric Drinking Fountains. Electric drinking fountains
shall be protected with ground-fault circuit-interrupter
protection.

Wait you said under. Does the receptacle feed/serve the fountain?

That is only section that relates GFCI directly to a drinking fountain and is for the drinking fountain only - and has no voltage or current limitations attached.

If a nearby receptacle not associated in any way with the fountain is present then we have to go back to 210.8 to see if any other conditions would make GFCI necessary.
 
Status
Not open for further replies.
Top