How to size the grounding conductor in switchgear?

Status
Not open for further replies.

zxfabb

Member
Location
LS
In IEC 61439-1, there is a sub-clause defining a minimum cross-sectional area of protective conductor PE or PEN. My concern is: are there any similar requirements in IEEE/UL standards or NEC? what is the practice in North America? Thank you.
Cross-sectional area of phase conductors mm2Minimum cross-sectional area of the corresponding protective conductor (PE, PEN) mm2
S < 16S
16 < S < 3516
35 < S < 400S/2
400 < S < 800200
800 < SS/4
 
Last edited:

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
Table 250.66 showing the grounding electrode conductor GEC form service equipment (generator or transformer or panel) to rod.
Table 250.122 showing the equipment grounding conductor EGC from equipment (other than service equipment) to previous breaker or last breaker.

If i understand you correctly, the connection inside the switchgear between the grounding & grounded conductor (neutral) is MBJ (main bonding jumber) shall be sized in accordance with 250.28(D)(1) through (D)(3).
 

Smart $

Esteemed Member
Location
Ohio
Yeah, I meant EGC. Thanks to you guys.
250.122 EGC are sizes based on the overcurrent protection device rating, not circuit conductor sizes.

250.66 for grounding electrode conductors and grounding bonding jumpers. It is based on the size of the ungrounded circuit conductors.
 