I'm new to posting here so please bear with me.
I'm dealing with a capacitor bank that serves a freezer warehouse approx. 100k sq.ft. When operating the PF is perfect. The cap bank fuses originally installed were 30amp and would occasionally pop on a single phase. Over time these fuses have been increased to 50amps, can't get a clear answer on who made this decision but this has resulted in (2) different trips by the fire dept. over a two year period.
.The over sized fuses are overheating and arcing. 50 amp fuses are not the solution.
I will be going back to the original configuration, 30 amp fuses.
The customer & I both understand the value of the cap bank but the question that I can't answer clearly to the customer is "what causes the fuse to trip".
I'm dealing with a capacitor bank that serves a freezer warehouse approx. 100k sq.ft. When operating the PF is perfect. The cap bank fuses originally installed were 30amp and would occasionally pop on a single phase. Over time these fuses have been increased to 50amps, can't get a clear answer on who made this decision but this has resulted in (2) different trips by the fire dept. over a two year period.
.The over sized fuses are overheating and arcing. 50 amp fuses are not the solution.I will be going back to the original configuration, 30 amp fuses.
The customer & I both understand the value of the cap bank but the question that I can't answer clearly to the customer is "what causes the fuse to trip".