Daikin, Manufacturer of a heat pump, wants to have a circuit protected by a 240 v. GFCI cir. br. feeding power to the EXO which has two 20 amp fuses in it. Does anybody out there know why they are asking for this? Does the NEC require all EXOs to have GFCI protection now?
No response from their email. No phone number for tech support.
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
Sounds like a manufacturer recommendation. I have never seen a heat pump on GFI, assuming an EXO is a ground water source heat pump?, that is up to the spec sheet. But still even those just get a regular breaker.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
Per 210.8(A)(3), all 15A and 20A, 125V receptacles outside of a dwelling unit has to be provided with GFCI [Ground-Fault Circuit-Interrupter Protection for Personnel.]
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I think NEC requires a receptacle outlet:
210.63 Heating, Air-Conditioning, and Refrigeration
Equipment Outlet. A 125-volt, single-phase, 15- or 20-
ampere-rated receptacle outlet shall be installed at an accessible
location for the servicing of heating, airconditioning,
and refrigeration equipment.
 

kwired

Electron manager
Location
NE Nebraska
I think NEC requires a receptacle outlet:
210.63 Heating, Air-Conditioning, and Refrigeration
Equipment Outlet. A 125-volt, single-phase, 15- or 20-
ampere-rated receptacle outlet shall be installed at an accessible
location for the servicing of heating, airconditioning,
and refrigeration equipment.

I don't think the OP is talking about a 120 volt receptacle, not sure what an EXO is but it apparently is 240 volt and has two 20 amp fuses in it.
 

StarCat

Industrial Engineering Tech
Location
Moab, UT USA
Occupation
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
Hmmm

Hmmm

Yes Augie....god the bloody acronyms....
Even at large they have been taken too far.
How about people start using words again so some of us can come up to speed.
Going on 30 years in HVACR and I have never heard that term, but I may not be up with current affairs.
? Electric Heat Accessory?............
This is a 3rd rate OEM.
I have to wonder what they are trying to " protect " and why this angle. What brought it about exactly.
 