Patient care area Class 1 controll circuit

Status
Not open for further replies.

pjs1554

Member
Location
Grand Cayman
I am installing a Lutron NOVA T dimmer with a Class 1 control circuit for the florescent cans in a patient care room. We will install the power 277volt for the cans in Hospital grade MC. They are connected to a normal power circuit. Do I need to install the 0-10 Volts Dc control circuit in Hospital grade MC as well? If not what wiring method is appropriate for this installation?

Thanks in advance to the help.

Best Regards

Paul
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
I would say yes, hospital grade MC cable or metal conduit would be required per 517.80:

Equivalent insulation and isolation to that required for the elecrical distribution systems in patient care areas shall be provided for communications, signaling, .....and systems less than 120 volts, nominal.
 