Industrial environment installed wet-cell storage batteries in a series configuration with a nominal 540VDC. Doesn't artical 480.7 require a "split string" connection to seperate the batteries to keep the battery group nominal voltage below 250VDC? Manufacturer isn't addressing this article requirement and says series connection is acceptable. Battery disconnect has a diagram on the door which shows configuraiton for both series and split connection.