I am adding a 70 amp circuit breaker to a 480V 800A 3 phase panel.  While searching online for a breaker, the description reads "70 amps at 40C".  I am assuming this means that the terminals are only rated to 40C.  Is that correct, or is the 40C a reference to ambient temperature?  If it is a terminal rating, now I am not sure how to properly size the wire, as the is no 40C column in table 310.15(B)(16)
	
		
			
		
		
	
				
			
				