The problem is we are dealing with 2 different things that are very similar.
The Subpanel has roughly 6 single pole Cutler Hammer BAB-C Switched Neutral Breaker and 6 2p 20amp Breakers in it.
All of these satisfy the requirement of disconnecting means.
The Single poles open the neutral when shut off and the 2p breakers feed onlly 240v loads so they are fine also.
Now for the Emergency Power Off. (If your planning on using a single pushbutton shut everything down)
To be able to shut off all the power coming out of the Subpanel you would either have to shunt trip the 1p Switched Neutral Breakers (Which I dont think they even make one) along with providing shunt trip coils for the 2p breakers and daisy chain the shunt trips all together so the EPO would kill them all, or, install a Shunt Trip in the Feeder Breaker feeding the Subpanel (But then you'd have to use one pole of the breaker to switch the Neutral ) or install a Contactor on the Line Side of the Feeder to the Subpanel and open the Neutral also or install a Contactor on the Load side of the Subpanel and run all the circuits through them or your goiing to have to install some type of manual disconnect.
My questiion is does the same rule apply for the Emergency Power off as for the Requirement for disconnecting the Neutral along with the Circuit Conductors for Maintenance Means?