ODonnell
 - Branson, MO, USA
I have a project for our theatre in Branson, MO. We are installing two new floor pockets on the stage which will require a connection through a fire-rated enclosed box to the actual electrical floor box which houses a 38-pin connector, 2-19 pin connectors for multicables for scenery, several other individual stagepin and twist lock connectors, all for dimmers and 3 or 4 20A circuits for constant power, PLUS, my problem, a 30A 3-phase, 5-wire, 208V(PPPNG), used for power for motorized scenery.
Most of these are no problem. the multicables cover the ratings needed for connections and the others are served by SO cable, all from the patch panel (which has the conduit runs from the dimmer patch bay and the breaker panel) to the actual electrical floor box (just under 3 feet long, 18 inches or so deep), in order to be able to easily swing the floor box all the way out of the stage to work on it. My issue with the 30A 3-phase is the limitation of the SO cord, when derated due to the 4 current carrying conductors, leads me to believe in order to correctly connect between the patch panel and the floor box, which all must be flexible, but cannot really be flexible conduit as the entire floor box actually swings completely over for service, and the space is very tight, i will need to go up to 6 gauge SO. I have this covered, but not in 5 conductor, only 4 conductor. We were thinking of running the ground parallel with the 4-conductor 6gauge SO. This way we have the ground wire with the cable, just not in the cable. The total distance this has to run would be 6 to 8 feet from the patch panel, clamped at the exit, through a small (6 inch) pipe, then clamped again at the electrical floor box entrance. That ground would be coming off a ground buss where all the grounds for each pipe feeding the patch panel land, including that for the 30-3phase.
Does anyone see any issue with this? Does anyone see any (cheap) alternative to needing 6-gauge SO to cover the 30-amp 5wire connection?
I wish there was more out there covering theatres. While we do have a small section and a nice load diversity rule we can follow for dimmers, there are always these special types of configurations for theatre that do not really have any direct answers. And the derating of SO cable is really, really harsh...