Yes and no.
The question is the extent to which the generators will share the load.
That will depend on their impedance, their regulating voltage, etc.
As long as the paralleling switchgear interfaces with the generator regulators and measures the current from each, you get the full sum.
If the switchgear just prevents an out of phase closure, no.