Had a call to check panel for some issues a home inspector brought up for house sale inspection.
Multiple grounds twisted together on panel.
They are. One went to the bar......some grounds are insulated , some not.
I know if the bar is rated for it you can put 2 grounds in one lug if same size conductor.....
Can you splice several grounds together instead and bring one ground to the bar?
There a combination of 12's and14's..........can I make a splice to one twelve and ground it, or is there an article stating all grounds in a panel must terminate on the ground bar?
There all too short to reach the bar.....do I have to install another one to the enclosure closer to where they reach?
AC--
Saw two 12's on a 30 two pole... they went outside to the ac. Not on list of what inspector picked up but for my own head, or if someone wants me to sign off on electrical and not just
invoice for repairs mentioned.
rheem ac at least 10 yrs old
v- 208-230 1 phase
compress rla 18
lra 104
fan 2 hp1/3
max fuse or brk 40
min fuse or brk 30
min. supply circ ampacity 25
the wire is 12-2 nm older........(might be thw)
should I rate that from the 75 degree column at 25 and that is actually correct? the outdoor disconnect is rated for 50a I believe...couldn't tell, it was mucked up alittle...
mabe 30.
There's one 12-2 AL nm wire on a 15a which seems to go to a whole house fan.... should be ok right.
Short of pulling the ladder out to crawl in the attic, seams there would be only two points to question in that circuit, that I could see, is if the switch was al/cu rated and if the motor
had to feed with copper conductors only ???
Thank You
Had a call to check panel for some issues a home inspector brought up for house sale inspection.
Multiple grounds twisted together on panel.
They are. One went to the bar......some grounds are insulated , some not.
I know if the bar is rated for it you can put 2 grounds in one lug if same size conductor.....
Can you splice several grounds together instead and bring one ground to the bar?
There a combination of 12's and14's..........can I make a splice to one twelve and ground it, or is there an article stating all grounds in a panel must terminate on the ground bar?
There all too short to reach the bar.....do I have to install another one to the enclosure closer to where they reach?
AC--
Saw two 12's on a 30 two pole... they went outside to the ac. Not on list of what inspector picked up but for my own head, or if someone wants me to sign off on electrical and not just
invoice for repairs mentioned.
rheem ac at least 10 yrs old
v- 208-230 1 phase
compress rla 18
lra 104
fan 2 hp1/3
max fuse or brk 40
min fuse or brk 30
min. supply circ ampacity 25
the wire is 12-2 nm older........(might be thw)
should I rate that from the 75 degree column at 25 and that is actually correct? the outdoor disconnect is rated for 50a I believe...couldn't tell, it was mucked up alittle...
mabe 30.
There's one 12-2 AL nm wire on a 15a which seems to go to a whole house fan.... should be ok right.
Short of pulling the ladder out to crawl in the attic, seams there would be only two points to question in that circuit, that I could see, is if the switch was al/cu rated and if the motor
had to feed with copper conductors only ???
Thank You