If I was sizing a 75 hp 3ph motor rated at 96 FLA> My wire size would need to meet 125% rule, which the amperage is 120Amps, which 1 AWG. My question is, if I need a non fused disco at the motor, the manufactures rating is 100a rated for 75 hp. But since I sized my wire to 120A (125%) do I need to bump to the next sized disco, which is 200Amp/125Hp? I dont believe I Have to, but just looking for some opinions.