StevenLeuck
Member
- Location
- Eugene, OR, USA
Call to Action / Potential Statewide Precedent re: NEC 334.10 & "Normally Dry"
To all,
Last week I posted a question under the "General Issues" section of this forum regarding the installation of Type NM-B before the building is "dried in". I received lots of great responses there and appreciate them all. From them and other information I had on hand I wrote an opinion email and request to the local inspectors and permitting authorities to permit us to rough-in with our Type NM-B cable before the roof of our 7 story project was on. On it's face it was denied. However, a follow up email to the chief code analyst resulted in them leaving the door open to our proposal provided we answer a few more questions about it. Their concern is that anything they decide here could become a precedent that will take root throughout the entire state of Oregon. They want to make sure they have good solid answers to their questions and concerns before authorizing us to proceed. They also suggested that it may be possible to authorize this one project as a limited observational test project to see how it goes.
I have attached a single PDF here with this post with the following documents (Note: This forum has a maximum size of PDF so had to break these all down into 1 page per file -- they are in numbered order -- apparently only 8 files max so will follow up with response to my own post with the remaining files):
1. My original email to the chief electrical inspector for the city.
2. A follow up email to the chief code analyst.
3. An article from the International Association of Electrical Inspectors citing a UL article.
4. A catalog submittal sheet from Southwire noting "Moisture Resistant" PVC sheathing.
5. A brochure from Underwriters Laboratory about storm damaged electrical work.
The Chief Code Analyst would like me to further submit the following information:
1. Something in writing from a manufacturer (preferably Southwire) that states that their Type NM-B cable is not affected by limited or incidental moisture such as might be had during the construction of a project but prior to a dry roof being installed (Note: The plywood decking of the floor above WILL be installed prior to our rough-in).
2. Evidence that other states or municipalities are allowing the installation of Type NM-B prior to the building being dried in.
3. Evidence that there are no chemicals in use during normal construction that when running together with the rain water could possibly leak onto the cable that would compromise it's integrity.
I am getting MSDS sheets from the general contractor's safety officer about potentially harmful products on site to answer #3 (we can't think of any really). What I am REALLY looking for and hoping you all can help me with is to get answers to the first two items on the analyst's list..... something from a manufacturer about Type NM-B's moisture resistance and a list of states or other municipalities that allow Type NM-B to be installed prior to drying in.
Unfortunately I'm on a tight timeline here. We're getting ready to start rough-in and a decision of this magnitude is going to take some time on the part of the inspectors to approve. If there is any information out there that you can contribute I would really appreciate getting it today if at all possible.
Thank you!
Steven Leuck
Owner
Contractors Electric, LLC
Eugene, Oregon
To all,
Last week I posted a question under the "General Issues" section of this forum regarding the installation of Type NM-B before the building is "dried in". I received lots of great responses there and appreciate them all. From them and other information I had on hand I wrote an opinion email and request to the local inspectors and permitting authorities to permit us to rough-in with our Type NM-B cable before the roof of our 7 story project was on. On it's face it was denied. However, a follow up email to the chief code analyst resulted in them leaving the door open to our proposal provided we answer a few more questions about it. Their concern is that anything they decide here could become a precedent that will take root throughout the entire state of Oregon. They want to make sure they have good solid answers to their questions and concerns before authorizing us to proceed. They also suggested that it may be possible to authorize this one project as a limited observational test project to see how it goes.
I have attached a single PDF here with this post with the following documents (Note: This forum has a maximum size of PDF so had to break these all down into 1 page per file -- they are in numbered order -- apparently only 8 files max so will follow up with response to my own post with the remaining files):
1. My original email to the chief electrical inspector for the city.
2. A follow up email to the chief code analyst.
3. An article from the International Association of Electrical Inspectors citing a UL article.
4. A catalog submittal sheet from Southwire noting "Moisture Resistant" PVC sheathing.
5. A brochure from Underwriters Laboratory about storm damaged electrical work.
The Chief Code Analyst would like me to further submit the following information:
1. Something in writing from a manufacturer (preferably Southwire) that states that their Type NM-B cable is not affected by limited or incidental moisture such as might be had during the construction of a project but prior to a dry roof being installed (Note: The plywood decking of the floor above WILL be installed prior to our rough-in).
2. Evidence that other states or municipalities are allowing the installation of Type NM-B prior to the building being dried in.
3. Evidence that there are no chemicals in use during normal construction that when running together with the rain water could possibly leak onto the cable that would compromise it's integrity.
I am getting MSDS sheets from the general contractor's safety officer about potentially harmful products on site to answer #3 (we can't think of any really). What I am REALLY looking for and hoping you all can help me with is to get answers to the first two items on the analyst's list..... something from a manufacturer about Type NM-B's moisture resistance and a list of states or other municipalities that allow Type NM-B to be installed prior to drying in.
Unfortunately I'm on a tight timeline here. We're getting ready to start rough-in and a decision of this magnitude is going to take some time on the part of the inspectors to approve. If there is any information out there that you can contribute I would really appreciate getting it today if at all possible.
Thank you!
Steven Leuck
Owner
Contractors Electric, LLC
Eugene, Oregon
Attachments
-
EmailToCity_20131217Reduced 1.pdf104.3 KB · Views: 0
-
EmailToCity_20131217Reduced 2.pdf67.5 KB · Views: 0
-
EmailToCity_20131217Reduced 3.pdf120.7 KB · Views: 0
-
EmailToCity_20131217Reduced 4.pdf73.9 KB · Views: 0
-
EmailToCity_20131217Reduced 5 - Copy.pdf98.6 KB · Views: 0
-
EmailToCity_20131217Reduced 6.pdf122.9 KB · Views: 0
-
EmailToCity_20131217Reduced 7.pdf127.4 KB · Views: 0
-
EmailToCity_20131217Reduced 8.pdf64.3 KB · Views: 0