Transformer Differential Relay Slope Characteristics
anaz
Saudi Arabia
Dear All
Can anyone help me,
1.how to calculate howmuch current we have to inject ( Idiff and Irest.) , to test the differential characteristics for simens diffrential relay 7UT613,setting:Idiff=0.3I/In,slope1=0.25,slope2=0.50,Basepoint1=0,basepoint2=2.5 and Idiff>>=11 I/In,inorder to plot the slope characteristics
transformer differential relay testing..
Dear all..
anybody have excel spreadsheet to do slope test for transformer differential relays (Siemens,ABB & Alstom make)
regards..
Anaz...
Slope settings compensate for CT errors! Can you provide specifics:
o Xfmr-size;
o Primary, Secondary, Tertiary (if any) kV;
o Pri'y, Sec'y, Tert'y, winding configuration (Delta or Wye);
o Pri'y, Sec'y, Tert'y, line-CT sizes and ratios!
Regards, Phil Corso
o Xfmr-size;40MVA
o Primary, Secondary, Tertiary (if any) kV;115/13.8kV,No teritiary
o Pri'y, Sec'y, Tert'y, winding configuration (Delta or Wye);Pri-Delta,Sec-Yn1
o Pri'y, Sec'y, Tert'y, line-CT sizes and ratios! Pri- 300/5A, Sec- 2000/5A
Relay settings are as given below
Idiff=0.3I/In,slope1=0.25,slope2=0.50,Basepoint1=0,basepoint2 =2.5 and Idiff>>=11 I/In
we are using 7ut613 siemens relay,manual shows Idiff=/I1+I2/, I rest=/I1/+/I2/ and i want to test slope for Single phase to Ground fault,Phase-Phase fault, and three phase fault
so,how to inject and how much amps.Also,how to find out kneepoint1 and kneepoint2
thank you sir
Anaz...
For ground-fault, the NGR value is needed!
Actually, you need Protective Relaying 101! For that I rcommend:
Prof J. Lewis Blackburn's, "Siient Sentinals" (ca 1957-1984)
The "Modern" Version is "Applied Protective Relaying"; Library of Congress # 76-6880!
Both texts have a Template which simplifies the Ratio-Check procedure!
Phil Corso