- Illinois
- retired electrician
That is their book to show you how to do it by hand. They also have software to do that.
When was the last time a contractor got a price from only one sales person?
I understand why you used the dc resistance, and 1 wire length, to be conservative, but so I know the facts, I really should be using the ac resistance, and 2 wire lengths if not using a FC calculator?
I also have seen your posts on including the motors in the calc's. thanks
I'm almost afraid to ask, What does or doesn't change when it is 277/480 single phase, and a vfd to run a 3 phase motor?
If this comment is related to the calculation that I posted, then elimination of the conservative measures would have resulted in a lower value. I used the DC resistance, knowing that it was lower than the AC impedance. That caused the calculation result to be higher than it actually would have been in the field. But that was OK by me, because I only wanted to show that the fault current at the equipment was lower than 10kA. Once I achieved that goal, it was no necessary to take additional steps to obtain an even lower calculated value. That is the nature of using conservatisms in calulations. Once you have a result you like, you can quit working.Some of the "conservative" measures taken simply give you a value on the safe side. If you want to eliminate those "conservative" measures your result will be a higher value but will be more accurate.
Kind of what I was trying to say, I think. If you use a conservative means that will have an error on the high side then the goals in most circumstances will be met, and the fault current rating of the equipment will not be exceeded, even though you don't have a calculation that is correct.If this comment is related to the calculation that I posted, then elimination of the conservative measures would have resulted in a lower value. I used the DC resistance, knowing that it was lower than the AC impedance. That caused the calculation result to be higher than it actually would have been in the field. But that was OK by me, because I only wanted to show that the fault current at the equipment was lower than 10kA. Once I achieved that goal, it was no necessary to take additional steps to obtain an even lower calculated value. That is the nature of using conservatisms in calulations. Once you have a result you like, you can quit working.
On the other hand, if I needed to include a 10% margin, and therefore needed the calculated result to be below 9kA, I would have used the AC impedance value. That may or may not have been enough, but it would have been a reasonable engineering approach to the problem.