Conductor sizing 375 foot run

Status
Not open for further replies.

Smart $

Esteemed Member
Location
Ohio
So #4's for each hot, a #4 for the neutral and a #4 for the ECG. Correct. Cb on separate phases. I'm not sure but I think both gate openers will operate together. I sized the #4 for starting amps for each motor. Now that I digest this I should size the conductors for running amps at 8.5 each reducing my wire size to #6's.
With both openers operating at same time, #6 for hots, #12 (or any size larger) for neutral, #6 for EGC...
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
So #4's for each hot, (1) #4 for the neutral and (1) #4 for the ECG. Correct.

That's what I would do and not play the "what if" or "balanced load" game. I would bet there is a decent chance that somewhere along the line, 120v loads will be added (receptacles for tools, lighting, etc). With you (4) #4s you are pretty much covered for most eventualities.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
That's what I would do and not play the "what if" or "balanced load" game. I would bet there is a decent chance that somewhere along the line, 120v loads will be added (receptacles for tools, lighting, etc). With you (4) #4s you are pretty much covered for most eventualities.
High five from me to you augie. Simple is elegant.
 

bob

Senior Member
Location
Alabama
Someone must save us form this absurd code requirement. If the op chooses to put a 60 amp breaker on the feeder, then his proposal as submitted would be correct according to 250.122(B). Just because he uses a 20 amp he must use #4 egc.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Someone must save us form this absurd code requirement. If the op chooses to put a 60 amp breaker on the feeder, then his proposal as submitted would be correct according to 250.122(B). Just because he uses a 20 amp he must use #4 egc.
OK, so table 250.122 ( 250.122(A)) allows #10 for this situation. I still do not see a problem with the general requirement, just because it has an apparently paradoxical result in the special case you cite.
 
Last edited:

bob

Senior Member
Location
Alabama
My on going complaint is that there is no scientific reason for the up sizing. If a #10 is good for a 60 amp breaker with #4 cu, why
isn't #10 ok for #4 cu on a 20 amp breaker. There is not engineering reason for the generalized rule. On very long circuit runs
it may be necessary to increase the EGC to reduce the touch potential at the fault. However, there is no reason to make the
size increase mandatory in every case. This paradox occurs many times when upsizing for VD.

GD, Your comment was " I still do not see a problem with the general requirement, just because it has an apparently paradoxical result in the special case you cite. ".
Can you give a more detail explaination of what you mean.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Can you give a more detail explaination of what you mean.
Sure.
The rule on proportional upsizing was a very easy rule to write and I think that in a large number of circumstances it will not end up requiring a larger EGC than the table would specify given that you simply put in a bigger breaker.
The table does not linearly scale the EGC size with the circuit amperage and perhaps more importantly the problem it is intended to address deals with the voltage divider effect and the resulting touch potential in the specific case that the hot conductor is larger than the wire size corresponding to the breaker size.

(Not a very coherent statement, sorry, I am listening to the MH streaming video at the moment....) :)
 

Smart $

Esteemed Member
Location
Ohio
Sure.
The rule on proportional upsizing was a very easy rule to write and I think that in a large number of circumstances it will not end up requiring a larger EGC than the table would specify given that you simply put in a bigger breaker.
The table does not linearly scale the EGC size with the circuit amperage and perhaps more importantly the problem it is intended to address deals with the voltage divider effect and the resulting touch potential in the specific case that the hot conductor is larger than the wire size corresponding to the breaker size.
IMO, should be removed and the leftmost column heading of Table 250.122 be modified to read:

Circuit Rating?
Not Exceeding
(Amperes)

Then add the footnote:

?Greater of the following:
(a) rating or setting of the overcurrent device in circuit ahead of equipment, conduit, etc.
(b) ampacity of the ungrounded conductors where 800 amperes or less
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I think I edited after you posted, but pretty much the same meaning.

Why ampacity before???

Because if you enter the table using derated ampacity it would tell you to use a smaller EGC for the same ungrounded conductor if the conditions are harsh.
That seems wrong to me.

Sent from my XT1080 using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
Because if you enter the table using derated ampacity it would tell you to use a smaller EGC for the same ungrounded conductor if the conditions are harsh.
That seems wrong to me.
But it is debatable whether using a larger size to compensate for adjustments and corrections is actually "increased in size".... and the conditions of use are not all that likely to change if the OCP rating is increased at a later date.

I also believe the conditional footnote would not permit a smaller EGC than "normal"... but please elaborate if you feel I am in error.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
And I am taking the view that if the size is increased for derating reasons or for voltage drop reasons the EGC size should end up the same.
The EGC will not be subject to the kind of long term overload that derating addresses and so does not need to be upsized for those reasons but should not be made smaller for the same reasons. Just my opinion.

Sent from my XT1080 using Tapatalk
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
That's what I would do and not play the "what if" or "balanced load" game. I would bet there is a decent chance that somewhere along the line, 120v loads will be added (receptacles for tools, lighting, etc). With you (4) #4s you are pretty much covered for most eventualities.

I agree, just do the simple thing, but I'm not understanding how/why anyone would be adding anything to the OPs circuit if it already is for a designated purpose... the gate openers.

That is unless he is running the circuit to a panel at the gate, which he did not state that.
I was thinking he probably was just running to the required disconnect(s) for the motors that open/close the gates. Especially since he stated MWBC for the motors.
 

Smart $

Esteemed Member
Location
Ohio
And I am taking the view that if the size is increased for derating reasons or for voltage drop reasons the EGC size should end up the same.
The EGC will not be subject to the kind of long term overload that derating addresses and so does not need to be upsized for those reasons but should not be made smaller for the same reasons. Just my opinion.
I understand... not saying my proposal is an all-satisfying approach, but rather a compromise. It would save having to upsize the EGC proportionately with the ungrounded conductor based on cmil. Instead it would just be upsized to otherwise normal EGC size using a higher rated ocpd.

For example, for a 20A circuit using #4 Cu to compensate for voltage drop, no derating, 75?C terminations, you could use a #8 EGC, opposed to a #4 EGC as it is currently required. This way, the EGC would still be compliant if the ocpd were upsized.
 