trobbins313
It is desired to add a load of 5MW (5000000 watts) at unity power factor to 25 MVA Transformer which is already carrying its rated load at Power factor 0.8 P.F. Lagging. In order not to exceed the transformer MVA Rating, static capacitors will also be added. Determine the minimum MVA rating of the capacitors.
Here is how I went about solving it then I got stuck;
Present KW = 25MVA x 0.8 = 20MW
(sqrt)25?+20? = 15MVA
20 MW + j15
+5MW +j0
= 25 + j15
(sqrt)25?+15? = 29.15 MVA but this is over the rating of the transformer.
Thank you!
Tim
20 MW + j15
+5MW +j0
= 25 + j15
Thank you!
Tim