Now that the Life Safety and Critical branches are no longer considered to be part of the Emergency system, I assume that this has at least two significant implications:
1. That paragraph 700.27 essentially requiring coordination to .01 no longer applies.
2. That feeders associated with these two, now subsets of the Essential Electrical System, do not need to be 2 hour rated. i.e. bad news for our Pyrotenacs sales guy.
Thanks,
Mike
1. That paragraph 700.27 essentially requiring coordination to .01 no longer applies.
2. That feeders associated with these two, now subsets of the Essential Electrical System, do not need to be 2 hour rated. i.e. bad news for our Pyrotenacs sales guy.
Thanks,
Mike