I don't normally do a lot of explosionproof work but here I have to replace this chem storage fridge.
It's a brand-new installation and a brand-new architect engineered building
The new unit is full explosionproof fittings. The is a replacement, the old unit had explosionproof fittings
I'm installing it and I notice that the lights in the storage room are not explosionproof lights
The fluorescent tube sparks so this seems to me to defeat the entire purpose of explosionproof fittings on the fridge
Also the fridge was connected to a common bell box with the explosionproof fittings. Would've thought it goes to some kind Appleton or Killark cast box.
Is this is safe and code compliant insulation w the extension ring and the lighting ?
On the net:
Class I, Division 1, Group B locations
All electrical wiring and conduit must conform to the National Electric Code Article 501
Only explosion-proof lighting fixtures are to be installed in a gas meter room and these must meet the requirements of the NFPA-70: National Electric Code for Class I, Division 1, Group D locations
Mechanical fans and detection equipment must be continuously monitored in case of failure. Alarms for trouble and failure must be installed in accordance with NFPA-72, National Fire Alarm Code.