Dishwasher Both GFCI and ARFCI 2014 NEC

Status
Not open for further replies.
I think this has been talked about but I'm ready to start working on my first 2014 NEC house. Does the dishwasher (hard wired) in a kitchen require both GFCI and AFCI protection.

Thanks a bunch.
 
Last edited:

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Under the 2014 code, yes, the branch circuit that supplies a dwelling unit dishwasher must have AFCI protection and the outlet that serves the dishwasher must have GFCI protection.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
And the GFCI must remain accessible.
...
Actually it must be "readily accessible", but if you have a first printing soft cover code book, you would not know that.

The text in the first edition only requires that GFCIs required by 210.8(A) though (C) be readily accessible.

Item #1 in Errata #2 corrects that printing error.
png;base64,iVBORw0KGgoAAAANSUhEUgAAAAcAAAAJCAIAAABxOqH0AAAAD0lEQVQImWP4jw0wDDFRANLnvETzxsJRAAAAAElFTkSuQmCC
1. In 210.8 change the reference in the first sentence from: ?210.8(A) through (C)? to ?210.8(A) through (D).?
 
Status
Not open for further replies.