This has been removed from 2014 edition. Does that mean connection can be made to the load side of GFP?
That is not just a regulatory provision, it is a practical provision.So in a commercial building where the main CB has a GFP, the only way to connect PV is the supply side? Is that correct?
Where the GFP is integral with the CB, yes. If it is a separate GFP relay, you can connect load-side between MCB and GFP... but physical means to do so will likely be restrictive.So in a commercial building where the main CB has a GFP, the only way to connect PV is the supply side? Is that correct?
If the PV does not also incorporate its own GFP (or even if it does) and it faults, then you could have unbalanced currents in the main breaker..
...causing a main trip without any faults anywhere in the rest of the system.