... I have a question about the feeder rule. Please see the attached document. Are the attached circuits legal usages of the feeder/tap rules? These circuits are for use in industrial control panels. ...
Give us a bit more about the context of your question:
These schematics are normal for every motor starter bucket in the US. Are you modifying the buckets to add the control xfm? Are you modifying Listed combination starters? Did they show up from the factory this way? Are these built to UL-508a, or maybe NFPA 79.
The only thing that the NEC would say is 240.21.B.1.
There are additional restrictions in NFPA 79 - and that 13A CB in the first schematic has the look of an NFPA79 industrial control panel.
So, what exactly is your concern?
ice
Give us a bit more about the context of your question:
These schematics are normal for every motor starter bucket in the US. Are you modifying the buckets to add the control xfm? Are you modifying Listed combination starters? Did they show up from the factory this way? Are these built to UL-508a, or maybe NFPA 79.
The only thing that the NEC would say is 240.B.1.
There are additional restrictions in NFPA 79 - and that 13A CB in the first schematic has the look of an NFPA79 industrial control panel.
So, what exactly is your concern?
ice
The only thing that the NEC would say is 240.21.B.1.
I don't think 240.21.B.1 would be the right NEC reference for two reasons. First, the conductors are tapped from a branch circuit rather than a feeder (at least for the one showing the motor.)
Second, they are a motor control circuit. 430.72(A) would be the place to look.
Thanks for your responses. The top box is going to over seas. We are a UL panel shop. We would like all of our control panels to meet NEC and UL requirements.
My concern is the conductor size to the transformers and are we correctly following the tap rules for reducing conductor sizes in both schematics.