Portable generator conductor rating
Struggling to understand 445.13..
445.13 Ampacity of Conductors. The ampacity of the conductors
from the generator to distribution devices containing overcurrent
protection must not be less than 115 percent of the nameplate
current rating of the generator
So, a portable generator rated for 7,500 running watts can sustain a 31.25A draw.
The customer currently has a 5,500 running watts genny, but they can possibly get a bigger one down the line.
Does that mean that we'll be running 8/3 between the L14-30R and the service panel, even though the 14-30R is rated for 30A, just because many gennys out there that use L14-30 are capable of sustaining a higher current?
445.13 only applies to the conductors fron the alternator terminals to the first OCP. The portable generators you are describing will have a cb on the gen frame.
I don't do much with residential grade portable gens, but I would think the gen CB feeding the L14-30 receptacle is 30A - size of the gen shouldn't matter.
ice
ice
Agreed, if the generator has OCD built into it then 445.13 doesn't apply.
ice
I agree. The CB on the generator takes the ampacity into consideration. In addition you probably can't buy a 30 amp power cord made with # 8 wire unless you make up your own.