Service Entrance Uninsulated Grounded

Status
Not open for further replies.
I am trying to decide if this is a safe installation and could use some help.
A 3 phase 430 Volt wye service entrance, dose the grounding conductor need to be insulated? As of right now the service entrance has 3 insulated phase conductor and one uninsulated grounding conductor running down a pole to a 100 amp disconnect. Is this uninsulated service entrance conductor allowed because the load being used is 480 volts and no 277 is being used? So no current flows on this conduct other than leakage and ground faults.
Maybe there is to different possibilities depending on if it was being used as a grounded and grounding needing insulation or just grounding which can be uninsulated?

Or am i overthinking this haha.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
A service does not have a grounding conductor, it would have a grounded conductor. The grounded conductor is not required to be insulated on the line side of the main bonding jumper, even where it is a current carrying conductor.
 