112KVA 480D ~ 208Y120 transformer feeding two panels

Status
Not open for further replies.

dxco

Member
Wasn't sure if I should post in NEC or engineering calc...
I am proposing to feed two panels from one 112KVA transformer - 480 Delta to 280/120v Wye
My plan is this:
480V protected with 175A breaker ~ 2/0 with 6AWG ground >
to primary side of transformer >
Secondary transformer to two 175A Main Breaker panels, each located less than 10ft from transformer (<10ft run) -
Secondary is 3P 4W 2/0 with 6AWG ground to each panel.

Is this scheme NEC compliant or do I need to add a panel between the transformer and the two 175A panels?


Thanks in advance - I appreciate any guidance I can get!
DX
 
Last edited:
Wasn't sure if I should post in NEC or engineering calc...
I am proposing to feed two panels from one 112KVA transformer - 480 Delta to 280/120v Wye
My plan is this:
480V protected with 175A breaker ~ 2/0 with 6AWG ground >
to primary side of transformer >
Secondary transformer to two 175A Main Breaker panels, each located less than 10ft from transformer (<10ft run) -
Secondary is 3P 4W 2/0 with 6AWG ground to each panel.

Is this scheme NEC compliant or do I need to add a panel between the transformer and the two 175A panels?


Thanks in advance - I appreciate any guidance I can get!
DX

Didn't check the sizes, but othervise you're good to go.
 

Smart $

Esteemed Member
Location
Ohio
Just curious how would you size the GEC and the system bonding jumper?
Both sized per 250.66. The GEC is sized based on total cmil of secondary conductors, but the SBJ size depends on whether installed at the source or at panels, same as GEC connection at panels using taps off of main GEC.
 

iwire

Moderator
Staff member
Location
Massachusetts
312A * 1.25 = 390A, next std OCD is 400A.

I understand I can protect it at 400.

What I am missing is the advantage in doing so. I still cannot load the transformer beyond 312 amps.

The two 175 amp breakers combined are capable of 280 amps continuous or 350 non continuous.

So I guess there would be a slight advantage if you had a continuous load over 280 amps but less than 312 amps and you wanted to run the transformer at close to 100% of it's rating.
 

nicholaaaas

Member
Location
Baltimore
I'm installing this setup right now. I ordered #6 equipment grounds. While I was putting them in a thought hit me that the grounds need to be good for the full load even though they feed separate panels. Mine are fed from a commoun trough

Sent from my SM-T217S using Tapatalk
 