112KVA 480D ~ 208Y120 transformer feeding two panels
dxco
USA
Dating
Wasn't sure if I should post in NEC or engineering calc...
I am proposing to feed two panels from one 112KVA transformer - 480 Delta to 280/120v Wye
My plan is this:
480V protected with 175A breaker ~ 2/0 with 6AWG ground >
to primary side of transformer >
Secondary transformer to two 175A Main Breaker panels, each located less than 10ft from transformer (<10ft run) -
Secondary is 3P 4W 2/0 with 6AWG ground to each panel.
Is this scheme NEC compliant or do I need to add a panel between the transformer and the two 175A panels?
Thanks in advance - I appreciate any guidance I can get!
DX
My plan is this:
DX
Didn't check the sizes, but othervise you're good to go.
Just curious how would you size the GEC and the system bonding jumper?
Both sized per 250.66. The GEC is sized based on total cmil of secondary conductors, but the SBJ size depends on whether installed at the source or at panels, same as GEC connection at panels using taps off of main GEC.
Thank You!
Thank You!
Thanks a Lot!
I appreciate the help. This forum is a great resourse.
312A * 1.25 = 390A, next std OCD is 400A.
I understand I can protect it at 400.
What I am missing is the advantage in doing so. I still cannot load the transformer beyond 312 amps.
The two 175 amp breakers combined are capable of 280 amps continuous or 350 non continuous.
So I guess there would be a slight advantage if you had a continuous load over 280 amps but less than 312 amps and you wanted to run the transformer at close to 100% of it's rating.
I'm installing this setup right now. I ordered #6 equipment grounds. While I was putting them in a thought hit me that the grounds need to be good for the full load even though they feed separate panels. Mine are fed from a commoun trough
Sent from my SM-T217S using Tapatalk
Each panel had a 200 amp breaker
The OP said each panel will have a 175 amp CB. In this case the OCPD size is irrelevant because he's sizing a supply side bonding jumper SSBJ not an EGC.