Got a call because a grain bin aeration fan wouldn't work. ( 230V 1ph, 10-15hp, 42-61FLA, SF1.0) Overload on starter was tripped, reset, and amp check was 74 amps. No brainer, checked capacitors, bad. Replaced run caps, and same result. 72-74 amps. I noticed I get a 7-12 volt drop when running 1 fan, but the same voltage with 2 both fans running (2 fans total on site.) Ran wire from panel to fan directly, no change. Had motor rebuilt, they only replaced a bearing, and said it was fine. So When POCO comes out, voltage drop isn't as severe that day (naturally), but they agree to upgrade XFMR, but asked if I will replace motor first. No problem, get new motor, and exact same amperage draw 72-74A. POCO changes XFMR, situation gets a little better 68-70A running now.
The service pole is about 250' from grain bins. The bin is fed with 4/0 CU conductors(2 ungrounded, 1 Neutral, no ground wire in the Feeder.) I do believe its in conduit underground, but cannot confirm as I haven't done any digging yet, but the conductor is THWN insulation, so Im hoping they weren't that stupid. I don't believe the voltage drop I have is normal with this size conductor, and I cant explain the over amperage.
Do I have a conductor going bad? The symptoms aren't that bad for me to suggest that, but Im running out of options. With the length Im talking here, whats the best way for me to do some tests (i do have multi meter, no megger.) I've contemplated laying conductor on the ground and testing, but that's a lot of wire and labor. I dont want to tell the owner new wire is the answer, when that might not fix the problem.