One of my students came up with this question and it baffled me...
Single phase, 15A, 120V circuit. Let's say we've calculated total voltage drop to not exceed 3%.
There are 2 circuit conductors, ungrounded and neutral. Assuming each wire was calculated separately:
a. Could we pull a #8 ungrd. conductor with a #14 neutral? Also according to 250.122, EGC would have to be a #8.
b. Could we pull a #14 ungrd. conductor with a #8 neutral? EGC could be a #14 in this case according to 250.122.
Both of these scenarios seem to be thwarting the system, but I can find anything in the code that would prevent it.
Help!