AFCI on MWBC

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
No theoretical reason why not. The arc signature will be the same.
If the breaker includes GFP, then the neutral must run through the two pole breaker, just like for a GFCI breaker.

Sent from my XT1080 using Tapatalk
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
GE uses 2 sp afci breakers with handle ties. I believe CH also makes a dp afci. Here is how ge does it.

ry%3D480
 