hbendillo
Senior Member
- Location
- South carolina
My firm has been asked to render an opinion on whether wiring in an existing facility, which is probably wired in Romex, will have to be replaced if the building is used as I-1 or R-4 occupancy for an assisted living facility. In my research so far, it seems that the deciding factor is the type of construction. Can't find anything in the building code that addresses wiring. It does not fall under the requirements for healthcare facilities in my opinion. 334.10(3) under Uses Permitted states "Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12."
So unless this is Type I or II construction it seems like romex is permitted. Does anybody have any information to the contrary?
So unless this is Type I or II construction it seems like romex is permitted. Does anybody have any information to the contrary?