distribution center ques?
wireman1
Does the code allow a 4,000 AMP 480 volt distribution center
located inside a plant to be in the open? Or, must it be in
a caged-off area with access doors for qualified personnel only?
site code article.
jim dungar
Wisconsin
PE (Retired) - Power Systems
site code article.
This is a design issue not covered by the NEC.
Local building codes may be applicable.
charlie b
Lockport, IL
Retired Electrical Engineer
The only relevant code article is 110.26, since the only relevant issue is working clearance. What you describe is perfectly acceptable, from the NEC perspective. The owner may wish to put a cage around the equipment to prevent inadvertent or malicious operation. But as has already been said, that is a design issue, not a code issue.