I have dealt with this situation frequently where two adjacent condos are purchased and combined.  I some case the owner retains two meters.  This, however,  incurs an  additional expense since around here there is a minimum monthly fee  ($15?) added on top of the monthly usage.  In other cases we have spliced the two feeders together within the meter bank so that one meter serves both condos.  The POCO installs a blank cover over the unused meter.  This method eliminates the additional monthly charge.
How do you handle:
230.70 General.
Means shall be provided to disconnect all
conductors in a building or other structure from the service entrance
conductors.
Would two separate 'main' panel inside = means (plural)? In this example.
230.72 Grouping of Disconnects.
(A) General. The two to six disconnects as permitted in
230.71 shall be grouped. Each disconnect shall be marked
to indicate the load served.
230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means for each service
permitted by 230.2,
230.2 Number of Services. A building or other structure
served shall be supplied by only one service unless permitted
in 230.2(A) through (D).
(C) Capacity Requirements. Additional services shall be
permitted under any of the following:
(3) By special permission
So would two disconnects be required outside or could you have them both inside and seperated in the above combined condo example?