RJH333
Member
- Location
- New Jersey
I have a metal stud wall with 4 inch square metal boxes on both sides on a demising wall in a residential application.
I asked the Fire inspector if I could putty pad the boxes that are with-in 24 inches. I have back to back kitchens and can not separate all of the outlets more that 24 inches.
He said because the wall is metal stud it is communicating and every box on both sides of the wall would have to be protected or the wall would have to be insulated with mineral wool. He is looking at IBC 713.3.2. He stated that the holes in the metal stud make it a communicating wall. There is a resilent channel on one side which would keep the rock off of the studs for sound reasons, and this would also allow heat and smoke to travel. This is the first time I am hearing of this we would always just putty pad the boxes with in 24 inches and be done. Anyone?
I asked the Fire inspector if I could putty pad the boxes that are with-in 24 inches. I have back to back kitchens and can not separate all of the outlets more that 24 inches.
He said because the wall is metal stud it is communicating and every box on both sides of the wall would have to be protected or the wall would have to be insulated with mineral wool. He is looking at IBC 713.3.2. He stated that the holes in the metal stud make it a communicating wall. There is a resilent channel on one side which would keep the rock off of the studs for sound reasons, and this would also allow heat and smoke to travel. This is the first time I am hearing of this we would always just putty pad the boxes with in 24 inches and be done. Anyone?