I am installing an exhaust fan for a commercial kitchen vent hood (Ansul) project. The exhaust fan is a 208V, 3-phase, .75 HP (3.5A) fan. I have sized the circuit breaker for the fan as follows:
Step 1 - Find the full load current from Table 430.250 which comes out to be 3.5A.
Step 2 - Use Table 430.250 to find the size of the inverse circuit breaker size (250%) so 3.5A * 250% = 8.75A
Step 3 - Go to 2406 for standard size OCPD size. Min size = 15A
Step 4 = Use 208V 3-pole 15 amp circuit breaker for the exhaust fan.
However, I am in a remote location in the Panshir Valley of Afghanistan and the 3-pole 15 amp circuit breakers have not come in. I do however have a 3-pole 20 amp circuit breaker. My conductor size is #12 THHN. I am wondering if there is a code compliant way to use the 3-pole 20 amp circuit breaker.
No, I do not have a fused disconnect available. And yes, the circuit is a dedicated circuit for the exhaust fan because it runs through the fire suppression panel.
Your expertise is sincerely appreciated.
Respectfully,
Cohosilver
I am installing an exhaust fan for a commercial kitchen vent hood (Ansul) project. The exhaust fan is a 208V, 3-phase, .75 HP (3.5A) fan. I have sized the circuit breaker for the fan as follows:
Step 1 - Find the full load current from Table 430.250 which comes out to be 3.5A.
Step 2 - Use Table 430.250 to find the size of the inverse circuit breaker size (250%) so 3.5A * 250% = 8.75A
Step 3 - Go to 2406 for standard size OCPD size. Min size = 15A
Step 4 = Use 208V 3-pole 15 amp circuit breaker for the exhaust fan.
However, I am in a remote location in the Panshir Valley of Afghanistan and the 3-pole 15 amp circuit breakers have not come in. I do however have a 3-pole 20 amp circuit breaker. My conductor size is #12 THHN. I am wondering if there is a code compliant way to use the 3-pole 20 amp circuit breaker.
No, I do not have a fused disconnect available. And yes, the circuit is a dedicated circuit for the exhaust fan because it runs through the fire suppression panel.
Your expertise is sincerely appreciated.
Respectfully,
Cohosilver