M mstrlucky74 Senior Member Location NJ Jan 26, 2014 #1 There is always going to be conduit(nipple) between the two panels to go from the feed thru lugs to the 2nd section correct? Thanks.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician (retired) Jan 26, 2014 #2 Not always but most of the time. I've seen them with windows cut out of the side of each panel. We typically use a RMC close nipple at the top and one at the bottom for the connection of the two sections.
George Stolz Moderator Staff member Location Windsor, CO NEC: 2023 Occupation Hospital Master Electrician Jan 26, 2014 #3 Sometimes there's three or four.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Jan 26, 2014 #4 A lot of the guys here use PVC "box adapters" and couplings between sections. Gives a nice smooth box entry that usually takes of less room than a nipple & bushing and I am told it's less expensive. http://www.carlonsales.com/techinfo/brochures/conduit/Conduit_Fittings_Schedule_40_and_80.pdf