I am surprised by sudden increase in the level of acetylene in one of our transformer. Since years we are regularly monitoring the DGA and have never come across any gas more than set limits of IEEE. The acetylene contents has gone around 50ppm within last four months.The transformer is for arc furnace application ( with onload tap changer) and still in working conditions. The winding resistance and TTR shows normal results.Documents and papers on internet tells that this gas is generated due to arcing inside the transformer along with hydrogen. I dont see any noticable increase in other gases like H2 or CO or CO2.This increase has been notices after recent oil filtration and manintenance of diverter switch of tapchanger by manufacturer of tap changer. I suspect that something has gone wrong during these activities but dont know what ?
The total dissloved combustible gases content very much below limit of 720ppm (IEEE).
I would like the experts here for their opinion for further actions .
The total dissloved combustible gases content very much below limit of 720ppm (IEEE).
I would like the experts here for their opinion for further actions .