Hendrix
- New England
Yea or Na.
Yea or Na.
Sorry I meant transformer.For starters, I don't know what TS stands for. But every building needs a disconnecting means. If the 6 dwelling units are separate buildings, then you need a disconnect for each. If they are within the same building, then you can have one disconnect shut off the entire building. But that would not be a good design. So exactly what are you asking?
The whole question was kind of cloudy, wasn't it.Sorry I meant transformer.
From the transformer secondary, to 6ix meter sockets, to six non attached dwellings with a main disconnect being at each dwelling instead of at the meters.
They are "heating it up" as we speak. I guess they allow it.I guess I misunderstood too as I assumed a 6 unit single building.
You could do without the main and put a main at each building and be compliant. You would then have service conductors to each building instead of a feeder and each building would have a separate service. But you better check with your POCO first as they may not allow it (many won't).
It is allowed... but the sections of Code involved depend on whether transformer is service (POCO or consumer owned) or a separately derived system. For the former, service conductor rules apply. For the latter, tap rules of 240.21(C) apply.They are "heating it up" as we speak. I guess they allow it.
What is "TS"? Hope it is not transfer switch. I think you mean transformer secondary.
If you just mean do you need a main ahead the 6 meters, no, you could use a MLO meter center with the breakers on the load side of the meters as the service disconnects since you are not exceeding six.
What if you had 7 or 8 meters on the back of a Single Bulidling that serviced 7 or 8 tennants in the same building? would you need a single main in the tap box of the Meter Center or not?
I'm going to go with "not necessarily". Consider that each is a permitted service entrance conductor and also subject to two to six disconnect grouping.I would think yes, 230.71.
If you put a main ahead of the building, wouldn't you be supplying the building with more than one feeder???
You're changing the parameters vs. the OP. Hard to get into specifics without getting issues confused. If you want to discuss this, suggest you start a new thread.A local power company here...