310.15 (B)(7) 120/240-Volt, Single-Phase Dwelling Services and
Feeders. For one-family dwellings and the individual
dwelling units of two-family and multifamily dwellings,
service and feeder conductors supplied by a single-phase,
120/240-volt system shall be permitted be sized in accordance
with 310.15(B)(7)(1) through (4).
(1) For a service rated 100 through 400 A, the service
conductors supplying the entire load associated with a
one-family dwelling, or the service conductors supplying
the entire load associated with an individual dwelling
unit in a two-family or multifamily dwelling, shall
be permitted to have an ampacity not less than 83 percent
of the service rating.
(2) For a feeder rated 100 through 400 A, the feeder conductors
supplying the entire load associated with a onefamily
dwelling, or the feeder conductors supplying the
entire load associated with an individual dwelling, unit
in a two-family or multifamily dwelling, shall be permitted
to have an ampacity not less than 83 percent of
the feeder rating.
(3) In no case shall a feeder for an individual dwelling unit
be required to have an ampacity greater than that specified
in 310.15(B)(7)(1) or (2).
(4) Grounded conductors shall be permitted to be sized
smaller than the ungrounded conductors, provided that
the requirements of 220.61 and 230.42 for service conductors
or the requirements of 215.2 and 220.61 for
feeder conductors are met.