I have to get 20' from the first floor to the third floor with a 70A 2p emrgency power 208v ct. for a UPS
All wiring originates from same 480V source... eventually!
I can core to get to the 3rd fl.
It would be more direct to use the 480v emergency power pathway, providing color to distinguish circuits, 600v insulation and so on.
Art. 300.3 C (1) 600volts, Nominal, or Less. Conductors of circuits rated 600 volts, nominal, or less ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Seems this 700-9(b) prohibits in this case when it says the e-ct " supplied from source distribution to load"
anything else?
(b) Wiring. Unless otherwise permitted in (1) through (4), wiring from an emergency source or emergency source distribution overcurrent protection to emergency loads shall be kept entirely independent of all other wiring and equipment. Wiring of two or more emergency circuits supplied from the same source shall be permitted in the same raceway, cable, box, or cabinet
anything else?