Devices on the doors of a purged panel

Status
Not open for further replies.

wireman

Inactive, Email Never Verified
Could I put a 24vdc powered HMI and 24vdc powered pilot lights on the door of a purged control panel if the power to these devices go through intrinsic barriers (also located in the enclosure)?

This would be in a Class 1 Div 2 (gases) area. The purge system would be a Type Z, which reduces the classification of the enclosure from Div 2 to non-hazardous.

The other hitch is the only power will be a battery inside the enclosure. The purged system can shut off the power leaving the battery but of course there would still be power available across the battery's + and - terminals. So technically I guess you could say not all of the power is disconnected inside the panel when it is not purged.

Any thoughts?
 
Could I put a 24vdc powered HMI and 24vdc powered pilot lights on the door of a purged control panel if the power to these devices go through intrinsic barriers (also located in the enclosure)?

This would be in a Class 1 Div 2 (gases) area. The purge system would be a Type Z, which reduces the classification of the enclosure from Div 2 to non-hazardous.

The other hitch is the only power will be a battery inside the enclosure. The purged system can shut off the power leaving the battery but of course there would still be power available across the battery's + and - terminals. So technically I guess you could say not all of the power is disconnected inside the panel when it is not purged.

Any thoughts?

Why not just buy an HMI that is already rated for C1D2? Many of them already are. many off the shelf HMIs are not suitable for use in a purged area as the membrane keypad and/or touchscreen overlay can separate from the internal pressure.

I am not sure the lights are an issue. You can buy them rated for C1D2 as well.

Normally a type Z purge system will not have any means to automatically shut off power.
 
Why not just buy an HMI that is already rated for C1D2? Many of them already are. many off the shelf HMIs are not suitable for use in a purged area as the membrane keypad and/or touchscreen overlay can separate from the internal pressure.

I am not sure the lights are an issue. You can buy them rated for C1D2 as well.

Normally a type Z purge system will not have any means to automatically shut off power.

Bob,
Thanks for your reply. A C1D2 rated HMI is certainly an option. What I haven't had time to look at yet is if one is available in a model similar to what else is used in the plant.
I'll look into the pilot lights.

As far as shutting off the power, from what I've read in P&F's literature about C1D2 Type Z systems: "power can be deactivated or an alarm must indicate a loss of pressure." Since the cart is portable they won't want to be dragging around a cable to attached to an alarm located somewhere else. Figured it would easy enough to just shut off the power.
 
Not sure the alarm would have to be remote. A local alarm on the cart would work if the area is occupied.
Otherwise a monitored wireless alarm connection should work, yes?

Tapatalk!
 
Not sure the alarm would have to be remote. A local alarm on the cart would work if the area is occupied.
Otherwise a monitored wireless alarm connection should work, yes?

Tapatalk!

maybe the rules have changed but the last time I did one of these no alarm was required at all. just indication.
 