2 bonding questions

Status
Not open for further replies.

tyha

Senior Member
Location
central nc
Ok guys. I'm back in the field after 10 yrs so cut me some slack..lol.
I'm coming out of a 120\208v switchboard with emt to feed a meter pack for some apartments. The switchboard is one of 6 service DS for this building fed directly from utility vault. Its a mixed use project with retail on lower level and apartments on upper levels. First question - do I need to bond the emt feeders going to the meter pack with a bond bushing in the swbd because the swbd is considered service equipment and secondly if we place a pull box on these feeders (6 parallels) due to number of bends do we need to splice the egc in the box and install bond bushings in the box. I'm thinking yes #1 and no #2 but as I said its been a long while. Thanks
 

Smart $

Esteemed Member
Location
Ohio
I agree... unless there is some reason the electrical continuity of the EMT to enclosure is compromised.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You would need something other than standard locknuts on the raceways that contain service entrance conductors. Beyond that you would have feeders and standard EMT connectors would be all that you'll need.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In reference to the 2nd part of your question, see 250.148
 