Aluminum vs Copper Ground/Neutral Bar
fifty60
USA
I have always used copper neutral/grounding bars. The n/g bar manufacturer is telling me that almost everyone nowadays are using Aluminum n/g bars. What factors should I consider here when evaluating a switch? Is his statement correct?
I don't think you will find a copper ground/neutral bar in much of anything these days. AL is a much better choice. It is less expensive and much easier to make it work with both copper and aluminum wires.
for the most part you can't put them in a US product anyway since they are only UL recognized, unless you are making a UL listed product that specifically allows for it.
You kind of lost me with the second half of your reply...You can't use copper or aluminum ground/neutral bars in US products? Also, I thought they had to be UL467 listed either way?
Sometimes it seems, we are often so used to sloppy language like "UL Approved", that when someone makes a correct statement it doesn't sound right. I think this is the third thread, I've read this morning, that deals with components rather than fully assemble products.
Terminology is very important.
http://www.ul.com/global/eng/pages/corporate/aboutul/ulmarks/promotional/mark3/#comp_recog
"These components are intended only for incorporation into other end-use products that may be eligible for UL's Listing, Classification or Certificate Service."
If they are UL Recognized then I have to used them in a UL listing eligible product? Or, do they simply loose their UL recognition if not incoporated into a UL listing eligible product. UL listed will not loose its listing if used in a non UL listing eligible product?
Can a standard be "recognized" or "listed"? For example, can a breaker be either listed or certified to UL 508?
The bars I am looking at "UL Recognized and CSA Certified for 600 Volts". Am I definitely wrong to think that the neutral ground bar has to be UL 467 listed or recognized?
UL recognizes parts that are intended solely to be incorporated into UL listed products. That is all recognition means. it does not mean you can put it in a UL listed product, or any other product for that matter. UL does not certify components or products. Listed or recognized are the two choices available.
Listed products such as UL508a control panels have a series of requirements that have to be met to meet the listing requirements. That includes what components you are allowed to use within that listed product. The UL requirements for the listed product will tell you very explicitly what component products can be used. Some components will be UL listed, others will be UL recognized. Some are neither. There will be directions in the listing standard that tells you what components can be used and in what way.
I don't know what UL standard your product is being listed to so I cannot tell you with any certainly what components are acceptable.
This is what UL508a says in part about grounding components.
14.2 An industrial control panel shall be provided with a field wiring terminal for the connection of an
equipment grounding conductor. The terminal shall comply with:
a) The component requirements of a field wiring terminal in accordance with Section 28, Field
Wiring; or
b) The requirements in the Standard for Grounding and Bonding Equipment, UL 467.
Table SA 1.1 lays out the parts you can use. I can't cut and paste from it because it is a formatted table and the forum does not allow most formatting.
For paragraph
14.2(a) Recognized Terminal Blocks UL 1059 XCFR2
14.2(a) Recognized grounding bar kits UL 67, UL 891 QEUY2 Procedure described only
14.2(b) Listed Grounding and Bonding Equipment UL 467 KDER
14.2(b) Recognized Grounding and Bonding equipment UL 467 KDER2
What does this mean? Well it means you can use these things for ground terminals for field wiring.
"Procedure described only" means UL has to specifically approve it. In practice it usually means if you pay them they will let you use it.
Just because the ground bar is UL467 (listed or recognized) does not mean it is Ok to use it in a UL508a control panel. It still has to be category code KDER or KDER2.
Most of the UL467 listed stuff I have run across is insanely expensive. I don't recall seeing any that are only recognized.
some ground/neutral bars are UL486 recognized.
lost my chance to edit. I wanted to add this.
Note the standard says you can use
a) The component requirements of a field wiring terminal in accordance with Section 28, Field Wiring
In table SA1.1 for section 28 it allows you to use the following items.
28.2.1 Recognized Terminal blocks UL 1059 XCFR2
28.2.2 Listed Pressure Wire connector UL 486 series ZMVV
28.2.2 Listed component provided with integral pressure wire connectors UL 486 Series
28.2.3 Wire Binding Screw UL 508A
So my take is you can also use UL486 listed connectors category code ZMVV.
the second thing listed under 28.2.2 is important because otherwise you would not be able to use the integral ground terminal often supplied on devices such as VFDs for field ground connections.
I am not sure what a wire binding screw even is.
I have the UL file number for the bar I currently use, and when I look it up it comes up KDER.file number, so I'm thinking that I have a listed under UL 467 category KDER. No where on the UL website does it say that the file number is listed under UL 467. Could the KDER mean anything else?
The panels are not UL 508, though I would like them to be someday. Some panels get UL inspected at the request of the customer, but most do not. I am in the process of CE marking, and I am using IEC-61010. UL uses this same standard for our equipment. It has a basic section on grounding and bonding, and then has a component requirements section.
The component needs to be tested to the relevent IEC standard
or tested to 61010 and the relevent safety requirements of the applicable standard
or tested to a non IEC standard that is equal to or greater than the relevent IEC standard.
Most UL listings and recognitions are adequate, as long as the application of the product does not negate the UL listing or recognation.
I have several issues with my equipment.
1) i currently use a copper grounding/neutral bar that has the KDER category listing. This bar accepts the grounded service conducter, and all of the accessible parts that are hazardous live are bonded to the same terminal bar. I would like to switch this bar to aluminum if possible.
2) I'm trying to bond all of my accessible and removable panels back (from the inside of the equipment) to this ground/neutral terminal. I have to install studs on the removable access panels, and also on the frame of the equipment. A conductor is then ran from the access panel to the frame. The frame is bonded to ground through the terminal on the sub panel. The resistance of the connection from the panel to the ground terminal has to be less than 100 milliohms.
The panels are powder coated, and it is complicated to get the studs on the panels and not have them covered with the powder coat. The frame is simply painted, and not as much of a challenge to reach a conductive surface. I can get the studs on the panels, but then have to worry about them rusting because of the exposed stainless steel where the stud is inserted for bonding.
UL will come out and inspect stuff on a one up basis but it is crazy expensive.
CE has nothing whatsoever to do with products meant for use in the US.
I don't know how people in Europe feel about it but in the US what you are describing is specifically forbidden by the electrical code and by every UL standard I have ever heard of.
You are only allowed to connect the grounded conductor to earth or ground at a single point and that is at either the service point or where the system starts if it is s SDS.
If you are bringing in a neutral or grounded conductor from outside the equipment and in anyway connecting it to the frame, that is a serious code violation, and potential safety hazard.
Unless your equipment is service rated, you are not allowed to land any service conductors in it at all, grounded service conductor or ungrounded service conductor. It is just not allowed.
There is no requirement in any code I have heard of for a 100 milliOhm bonding connection. It may be an equipment spec. My suggestion is get a stud welder and weld a SS or brass stud to the frame if you are unable to connect to it in some other way. personally, unless there is an equipment spec that requires the bonding wires, I would not put them in. the fasteners that hold it together are probably quite adequate.
Yes, I understand. For my equipment, UL uses UL-61010 as our product standard. For CE marking, I use BS-EN61010 as our Harmonized Standard. Both are word for word the same, and are IEC-61010. For CE, I components (where safety is a consideration):
So I need to have components that are used for grounding and bonding comply with one of the above.
The equipment is permanently connected to a disconnect, 3 phase conductors and a green conductor are fed to the equipment. I call the green conductor a "service ground", so please correct me if I am wrong. I believe this green conductor is grounded back at its source, the secondary of the service transformer. This green conductor is connected to what I call "the protective conductor terminal" on the sub panel of the equipment. This protective conductor terminal is the top terminal of the UL listed ground/neutral bar. The bar has 14 input terminals.
Any panel components that have grounding studs are also connected to one of the open positions on this terminal bar. The frame is not normally directly connected to the terminal bar, unless an inspector requests us to connect the frame and the removable panels to the terminal bar. Everything is already connected to the frame by metal to metal contact, but this connection does not always satisfy the inspectors so they make us run seperate conductors. These seperate conductors from the panel and frame are what I am talking about.
I do not currently ground the removable access panels to the frame, but if I wanted to is 200.2(B) forbidding this type of connection from the access panels to the frame and then to to the main equipment neutral/ground bar?
200.2(B) Continuity. The continuity of a grounded conductor
shall not depend on a connection to a metallic enclosure,
raceway, or cable armor.
I have to go with a direct connection to a terminal on the bar?
You have a major problem with English and technical words and phrases.
A grounded conductor is not the same thing as an equipment grounding conductor (EGC).
Most times the neutral in a circuit is the grounded conductor, although the grounded conductor is not always neutral. In the US it is generally white in color. It has to be a wire or bus bar.
The EGC is the green wire, or sometimes green with yellow, or bare conductor. The EGC does not have to be a wire or bus bar. The frame can sometimes serve as an EGC, as can metallic conduit and various other conductive metal parts.
I suggest that you get out your UL508a spec and the NEC and read carefully the definitions sections. I think that would help both you and us. It is very difficult to help you when you are not using standard terminology.
Another problem is that you mix up concepts from Europe with the US. Anytime you use the term "CE" I cringe. It is completely and totally meaningless in the US.
200.2(B) is from the NEC. As a practical matter, it has no bearing on the equipment you are making. You have to make it to the UL standard for use in the US. The NEC is for electrical installations only. It has almost nothing to do with equipment standards.
I am referring to Equipment Grounding Conductors, and will hence refer to them as such. Sorry to make you cringe at CE, but please understand the the standard I am using is IEC 61010. 61010 has its own terminology and definitions. This standard is used by UL as UL-61010, and is also used as a harmonized standard to the Low Voltage Directive as BS-EN-61010. I am not mixing US and CE Marking, but the standards are word for word the same standard.
Inside of my equipment, I am trying to adhere to IEC-61010. Neither NFPA 70 and NFPA 79 apply absolutely to the inside of my equipment, but I try to apply their reasonings and statutes where relevent. A lot of the 61010 standard is clear, a lot of the standard is vague, and where it is vague I have to be able to explain my applications. Your explanations help a great deal towards this goal. To be honest, I probably gain more "intuition" from this site than anywhere else. I hope to someday be as technically omnipotent as a lot of people on this forum, but not quite there yet.
Is it correct to refer to the Equipment Grounding Conductor Terminal as the "Neutral/Ground Bar"?
The problem is that CE means nothing here. bringing it up just clouds things.
If 61010 is the equipment standard you are using than that is what you have to follow, regardless of what might be in NFPA70 or NFPA79.
It is not at all unusual for equipment standards to vary (sometimes a lot) from either of these two standards. Trying to shoehorn 61010 into the framework of NFPA70 or NFPA79 probably just won't work. In fact, neither of these standards apply to your equipment at all.
NFPA79 is an equipment standard that applies to industrial machines, much like 61010 applies to certain lab equipment. Trying to apply NFPA79 to lab equipment would be as absurd as trying to apply 61010 to industrial machines.
The NEC is not an equipment specification at all. It is an installation specification. It pretty much stops at where you hook the power up to the equipment covered by 61010.
For 61010, it is called the "Protective Conductor Terminal". Bonding the frame to this terminal, and then bonding the removable panels individually to the frame is not forbidden in 61010. But, you shouldn't do something simply because you "can".
My two open question on this thread are: 1) cosniderations for switching from copper to aluminum for the protective conductor terminal. 2) considerations for bonding the panels to the protective conductor terminal through the frame. I've already received a lot of help on this thread, but still think there are more considerations to be made.
Generally these kind of considerations are economic in nature.
Would I need to take into consideration the type of metal used for my conductors? Would it be a problem to use all copper conductors on an aluminum protective conductor terminal?