mkgrady
 - Massachusetts
This is a large home where the customer has a 400 amp service and two 200 amp MCB panels off the meter. I can't think of any code issue with installing two generators and two 200 SE rated transfer switches (ATS'S). At this point the plan is to use 2-20KW generators.
The point of using two generators is to conserve propane. He wants to be able to power most things in the house when there is reason to believe the outage will be brief enough that he will not run out of propane before power is restored. If the duration is long or looks like it could be he wants to shut off the less essential generator to conserve fuel.
So in this case I would put the most essential loads on generator 1 and MCB panel 1, and I would put less essential loads on generator 2 and MCB panel 2. That still leave lots of non essential loads on each panel that are too large for the generator output. The plan for that is to use load shed relays. The typical generic units allow for controlling two AC systems and up to four additional large loads.
I figure out of the 80 or so branch circuits I will wind up moving about half of them to the correct panel. That will be a lot of work that I wish could be avoided. The space needed for all the hardware required also concerns me but I think is doable.
Any thoughts on code issues or a better way to plan this job would be appreciated. Thanks