SUPPLY PANEL FEEDER BREAKER ATTACHED TO BUS BAR AND NOT AT TOP OF BREAKER

Status
Not open for further replies.

fun ee

Member
Location
Texas
Can a feeder supplying power to panel be connected to a branch circuit breaker or does NEC 408.36 or any other code paragraph disallow this?

Thanks Again.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I may misunderstand the question, but a breaker is not in itself a branch or feeder breaker.
A 50 amp breaker would be the same for a feeder or a branch circuit.... it depends on how it's used... see the definition of a branch circuit and feeder.
 
Last edited:

resistance

Senior Member
Location
WA
I assumed the OP was asking if it can be used as a main disconnect. Yet, I haven?t looked at the NEC section in question
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The code section mentioned requires an OCPD at any point along the path of the panel feeder. The panel itself does not require a main OCPD.
 

jxofaltrds

Inspector Mike®
Location
Mike P. Columbus Ohio
Occupation
ESI, PI, RBO
Could he be trying to have another source of power - like a generator?

The question is confusing. He is using 408.36 like it disallows what he is doing??????
 