F fun ee Member Location Texas Feb 11, 2014 #1 Can a feeder supplying power to panel be connected to a branch circuit breaker or does NEC 408.36 or any other code paragraph disallow this? Thanks Again.
Can a feeder supplying power to panel be connected to a branch circuit breaker or does NEC 408.36 or any other code paragraph disallow this? Thanks Again.
resistance Senior Member Location WA Feb 11, 2014 #2 fun ee said: Can a feeder supplying power to panel be connected to a branch circuit breaker or does NEC 408.36 or any other code paragraph disallow this? Thanks Again. Click to expand... You can use a breaker lock down
fun ee said: Can a feeder supplying power to panel be connected to a branch circuit breaker or does NEC 408.36 or any other code paragraph disallow this? Thanks Again. Click to expand... You can use a breaker lock down
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 11, 2014 #3 I may misunderstand the question, but a breaker is not in itself a branch or feeder breaker. A 50 amp breaker would be the same for a feeder or a branch circuit.... it depends on how it's used... see the definition of a branch circuit and feeder. Last edited: Feb 11, 2014
I may misunderstand the question, but a breaker is not in itself a branch or feeder breaker. A 50 amp breaker would be the same for a feeder or a branch circuit.... it depends on how it's used... see the definition of a branch circuit and feeder.
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Feb 11, 2014 #4 I think he is talking about backfeeding a breaker.
augie47 Moderator Staff member Location Tennessee Occupation State Electrical Inspector (Retired) Feb 11, 2014 #5 That makes more sense..... thanks
resistance Senior Member Location WA Feb 11, 2014 #6 I assumed the OP was asking if it can be used as a main disconnect. Yet, I haven?t looked at the NEC section in question
I assumed the OP was asking if it can be used as a main disconnect. Yet, I haven?t looked at the NEC section in question
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Feb 11, 2014 #7 The code section mentioned requires an OCPD at any point along the path of the panel feeder. The panel itself does not require a main OCPD.
The code section mentioned requires an OCPD at any point along the path of the panel feeder. The panel itself does not require a main OCPD.
jxofaltrds Inspector Mike® Location Mike P. Columbus Ohio Occupation ESI, PI, RBO Feb 12, 2014 #8 Could he be trying to have another source of power - like a generator? The question is confusing. He is using 408.36 like it disallows what he is doing??????
Could he be trying to have another source of power - like a generator? The question is confusing. He is using 408.36 like it disallows what he is doing??????