Hi all......
Reminds me of the Abbott and Costello skit ....up on the left leg.... " I Dream of Jeannie with...".. anyway
Read this and was wonder what this was about...... any thoughts......
thanks.
Residential Home 240v
About 200 feet from street
Meter and transformer on pole with underground 2/0 gauge cable approx 35 feet to panel in interior of home.
While loading one leg 15A I get a voltage rise on the other leg of 2.3 volts./While dropping the loaded leg roughly the same.
This would suggest a resistive neutral or improper size conductor.
However I am taking the measurement at the cables themselves which due to their size the rise on the unloaded leg should be negligible such as .25 volts.
With both legs unloaded and measuring at the cables I have 240V
One leg 121V the other 119V give or take a tenth or two.
I know the dangers of open or resistive neutrals I called the power company
Which came out and tightened up everything in the meter panel.
Who also had 121 and 119 leg voltages with no load.
The did not load test.
I still have the rise on the other leg when applying a load.
I was told as long as I didnt go over 125V on the other leg it wasnt a concern.
Which I could agree with except I am taking my measurements right at the cables,Which eliminates corrosion or a loose connection in the Main panel in the home
Since neutral has to only carry the imbalance in this case 15A and I am getting a fair rise I suspect an issue somewhere.
We already know we have an imbalanced {without load} transformer atop the pole.
Is this normal?
But more importantly the voltage rise{under load} is occurring from the meter back to transformer when a load is applied ...unless my underground cable is corroded and only has a strand or two left..which I highly doubt.
thanks.
Is this normal?