Axial flow & VFD

Status
Not open for further replies.

kwired

Electron manager
Location
NE Nebraska
Ok, we know an axial flow fan reacts differently to restricted air flow than a centrifugal. Should I be using the VFD settings for "general purpose", "fan/pump" or "High torque"?

My SEWAG, is not High Torque. I would used that for an auger that starts fully loaded.


I definitely agree it is not high torque, I'm guessing it is not constant torque but is still variable torque application, meaning the amount of torque necessary changes as other conditions change. I have never set up any fan as anything but variable torque when controlling with a VFD.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I definitely agree it is not high torque, I'm guessing it is not constant torque but is still variable torque application, meaning the amount of torque necessary changes as other conditions change. I have never set up any fan as anything but variable torque when controlling with a VFD.
The power requirement curve for an axial flow fan is not the same as a centrifugal fan for sure, it is flatter, even more skewed to being the OPPOSITE of a centrifugal fan depending on the pressure requirements it is used for. So from that standpoint, it is a "constant torque" looking application.

But from the VFD standpoint, the term "Constant Torque" and "Variable Torque" really is a misnomer, because the VFDs are CAPABLE of delivering either. The terminology for VFDs has to do with the OVERLOAD capacity of the drive itself. So because it is virtually impossible for a true centrifugal machine to overload the VFD at reduced speeds, there is no need for the VFD to be sized to deliver that overload capacity, hence we call it a "VT" or "Pump / Fan Duty" drive and up-rate the HP capacity. From that aspect, an Axial Fan is the same as a Centrifugal Fan, you cannot overload it, so the VFD does not need to be capable of the added OL capability inherent in a "Constant Torque" rating.

Bottom line, you can use a "Variable Torque" / "Fan and Pump" / "Normal Duty" rated VFD on an axial flow fan.

The same is not true of Axial Flow PUMPS, by the way, and may be what is behind your thoughts. The difference is, liquids can't compress like gases (air), so a flow restriction in an axial flow pump CAN result in an increase in load of the pump, so the VFD must be sized for that.
 

kwired

Electron manager
Location
NE Nebraska
The power requirement curve for an axial flow fan is not the same as a centrifugal fan for sure, it is flatter, even more skewed to being the OPPOSITE of a centrifugal fan depending on the pressure requirements it is used for. So from that standpoint, it is a "constant torque" looking application.

But from the VFD standpoint, the term "Constant Torque" and "Variable Torque" really is a misnomer, because the VFDs are CAPABLE of delivering either. The terminology for VFDs has to do with the OVERLOAD capacity of the drive itself. So because it is virtually impossible for a true centrifugal machine to overload the VFD at reduced speeds, there is no need for the VFD to be sized to deliver that overload capacity, hence we call it a "VT" or "Pump / Fan Duty" drive and up-rate the HP capacity. From that aspect, an Axial Fan is the same as a Centrifugal Fan, you cannot overload it, so the VFD does not need to be capable of the added OL capability inherent in a "Constant Torque" rating.

Bottom line, you can use a "Variable Torque" / "Fan and Pump" / "Normal Duty" rated VFD on an axial flow fan.

The same is not true of Axial Flow PUMPS, by the way, and may be what is behind your thoughts. The difference is, liquids can't compress like gases (air), so a flow restriction in an axial flow pump CAN result in an increase in load of the pump, so the VFD must be sized for that.
Is an axial fan loaded by pressure, volume of air flow, combination of both? This was brought up in a thread a while back with someone having trouble with an overloaded axial fan motor for grain aeration fans, I suggested restricting air flow which I know works with centrifugal fans, but received some opposition to that theory working for axial fans.
 