The minimum feeder-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less than the noncontinuous load plus 125 percent of the continuous load.
Exception No. 1: Where the assembly, including the overcurrent devices protecting the feeder(s), is listed for operation at 100 percent of its rating, the allowable ampacity of the feeder conductors shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load.
The commentary that I look at in relationship to this discussion is comparing the statement to the exception. Sizing the feeder min if equipment (over current devices) are rated not at 100% then the load plus 125% of the continuous load must be consider in the general rule. Compared to the exception when the equipment is rated at 100% then the ampacity of the ungrounded feeder conductor is based on the continuous loads plus the non-continuous loads without the 125% multiplier