Wye Distribution to Delta Transformer
Target1
United States
You can connect a delta to wye transformer (delta prim 12470 / wye secondary 480/277) to a wye distribution system correct? Distribution is at 12470...
Thanks!
No, I am doing:
WYE 12470 (distribution from the pole from utility) and connecting it to a 12470Delta / 480(277Y) transformer to connect as a wye to wye switchgear and then serves wye loads.
This is a typical connection, correct?
Edit1: I am just trying to make sure it is ok to connect a delta to wye transformer to a wye source ?
Thanks
I misunderstood your topology.
I will guess that the 12470V wye will be N-G bonded upstream somewhere at the service.
Then you situation will be fine / typical. Bond the N-G again at the secondary of your D-Y transformer